DIGITAL - Iconics Suite - SNMP Connection with eWon

Iconics Suite - SNMP Connection with eWon

Summary: this document describes how to connect with eWon router using SNMP Connection 

MIB file for SMNP connection to eWon you can find on HMS website


eWon configuration 


Configure SNMP communication in eWon webserver - Setup - Main - SNMP
Fill Community settings and host IP that will be allowed to access eWon 




Iconics Configuration in Workbench

Load MIB file




In Iconics add new Network in Data Connectivity - SNMP
In discovery setting 
Network: eWon's IP address
In SNMP select SNMP version based on which version is supported by device. Ewon supports SLMP v1
Select the Community you want to connect to 


























Then new device need to be added to the network 
You can add the device manually - right click on network you have created and select Add Device
You can also Explore Network to detect available devices automatically



In device settings select device type you connect to, SLMP version, IP Address of device and port number (default port number for SLMP community reading is 161)



Check the connection


In data browser (for example in data explorer tool), check the quality of the connection 
A list of accessible tags should be available 


    • Related Articles

    • Iconics Suite - Melsoft connection with iQ-R

      Detailed description how to configure connection between Iconics Suite SCADA and iQ-R PLC controller using Melsoft Connection Remember that your PC has to have the static IP address in the same subnet as PLC. iQ-R PLC default address is 192.168.3.39 ...
    • Iconics GENESIS V11 - Installation guide

      This article will guide you how to prepare your operating system and database to install Iconics GENESIS Version 11. If you need help with installation of an older version of Iconics, please follow this article instead: ...
    • Iconics Suite - Melsoft connection with FX5

      Detailed description how to configure connection between Iconics Suite SCADA and iQ-R PLC controller using Melsoft Connection Remember that your PC has to have the static IP address in the same subnet as PLC. FX5 PLC default address is 192.168.3.250 ...
    • Iconics Suite - MODBUS connection with FX5

      Detailed description how to configure connection between Iconics Suite SCADA and FX5 plc controller via MODBUS. FX5 side configuration Open Your FX5 project in GX Works3 to add new MODBUS connection. Go to the Navigation tree -> Parameter -> FX5UCPU ...
    • Iconics Suite - Connecting MX OPC Server UA to the Iconics Suite [Iconics Suite connection]

      This article show how to connect the MX OPC Server UA to the Iconics Suite/ Genesis64 application. Confirm that Your MX OPC Server UA i running. If You can see the MX OPC icon in the tray that mean the server is running. Run Workbench and go to the ...