GOC43 - Communication - Modbus Master (Client)
This article will guide you how to prepare GOC43 Modbus Client communication with FX5U (Modbus server) step by step.
Alert
Copyright © Mitsubishi Electric Europe B.V.
These Function Blocks / programs are demo versions that are only  intended to demonstrate program functions and provide general orientation for  your software choices. They are not suitable for use in real applications! "
1. Setup GOC 43 Modbus TCP Master
1.1 Create new project
      Select template project icon and give a name to your project.
      Select the GOC43 target version , and prefered programming languages. (This example we won't write any line of code)
1.2 Add Modbus Master device to Communication
      Select Ethernet from the Devices tab of the left project tree with right mouse click. Chose Add device..
      From fielbuses tree find modbus master and add device to the Ethernet configuration.
1.3 Add Modbus Slave device under Master device
      Select Master device and right click. Add Slave device under Master configuraton
1.4  Master device parameters
      1.4.1 General settings
            Leave everything default, only modify if you not statisfied these settings.
      1.4.2 Modbus TCP Master I/O Mapping
            For Modbus Bus cycle options choose Main task.
1.5  Slave device parameters
      1.5.1 General
            Set IP address of the slave device and port number (def :502)
      1.5.2 Modbus Slave Channel
            Set 1 channel for read (4 Holding register) and 1 channel for write (4 Holding register)
            In the IO mapping windows you can check your final setup.
1. 6 Login and download project
      1.6.1 Establish connection with GOC43
      Select device, then scan your network searching for PLC.
      1.6.2 Setup your PLC parameters
      1.6.3 Login and download project
      1.6.4 Start PLC
      Click on the "play" icon
      During download you will see the GOC system menu. After that screen will be white, because we did not add any visualization element to the project.
2. Setup FX5U Modbus TCP Slave
      2.1 Create a new project
      2.2 Setup Ethernet
            2.2.1 Set IP address of the PLC and subnetmask
            2.2.2 Add modbus connection to the ethernet configuaration window
                  Finish setup with pressing the Apply button
            2.2.3 checiking Modbus register allocation
                  Leave default
     2.3 Compile and download
                  Select parameter + program
                  Accept all pop up window, and follow reset instruction. (Reset method: Run-stop-reset switch hold down till error LED lit on the PLC  2-3 times then switch to RUN state)
3. Test
      3.1 Use IEC Objects for communication monitoring
      3.1 Write Values to FX5 PLC
            Prepare some value directly to cyclic exchange registers
            Check them in GX Works 3 buffer memory windows.
    3.2 Read Values from FX5U