1.3 Slave device parameters
1.3.1 General settings
Leave everything default, only modifyUnit ID: 1
1.3.2 Modbus TCP Slave I/O Mapping
1. 4 Login and download project
1.4.1 Establish connection with GOC43
Select device, then scan your network searching for PLC.
1.4.2 Setup your PLC parameters
1.4.3 Login and download project
1.6.4 Start PLC
Click on the "play" icon
During download you will see the GOC system menu. After that screen will be white, because we did not add any visualization element to the project.
2. Setup FX5U Modbus TCP Slave
2.1 Create a new project
2.2 Setup Ethernet
2.2.1 Set IP address of the PLC and subnetmask
2.2.2 Select Simple CPU
communication and set parameter to Use.
Then doublle click on detail settings.
2.2.3 Setup read and write parameters
Read
Write
Holding and input registers
2.3 Compile and download
Select parameter + program
Accept all pop up window, and follow reset instruction. (Reset method: Run-stop-reset switch hold down till error LED lit on the PLC 2-3 times then switch to RUN state)
3. Test
3.1 Use IEC Objects for communication monitoring
If everything fine, FX5U has to be connected to GOC43
3.1 Write Values to FX5 PLC
Prepare some value directly to cyclic exchange registers
Check them in GX Works 3 buffer memory windows.
3.2 Read Values from FX5U