The article describes the impact of the MC/MCR parameter (master control instruction) in the function block on the output signals and compares the influence of this parameter depending on the selected language (FBD/ST).
FB Type
Using FB as
a Macro Type, it is possible to use MC/MCR to control EN. The tests presented
below were performed for 2 FB (1 - Use MC/MCR to control EN; YES and 2 - Use
MC/MCR to control EN; NO) implemented as FBD/LD, as well as for the next 2 FBs
implemented in ST language.
The program of a macro type function block is loaded
by a calling source program along the execution flow. At the time of program
execution, the loaded program is executed in the same way as the main program.
MC/MCR Instruction
The tables show the impact of the MC parameter on the
signal outputs. All signals are presented in the order they were activated,
following the direction of the arrow.
Briefly,
for an FB implemented in FBD with MC/MCR - ON, the activation of the M100
output is only possible when both the M1 contact and the block input are in a
high state. If either M1 or M10 is in a low state, the M100 output will also be
in a low state.
When this
function is disabled (MC/MCR - OFF), the M200 output will be high when the
block input (M20) and the M2 contact are both on. Once the block is on, switching
the M2 contact will change the state of the M200 output. However, if M20 is
turned off after M200 is activated, the M200 output will turn off the next time
the M2 contact is off, and we turn on the block input at bit M20.
Importantly,
there is no difference in the result of the output signals when the FB
is written in the ST language. This is because the compiler converts the
bit-setting instruction into a MOV instruction.
Related Articles
iQ-R - FTP Server using SD card
This article explains how to prepare the iQ-R PLC to use the FTP Server function with access to files on the SD card. 1. FTP Server configuration in Module Parameter First, go to the Module Parameter window to enable the FTP Server. You can also ...
INV - FR-A800 - Master Slave Synchronization - Changing rotation direction
In this article I will describe how to change rotation direction of Slave inverter during synchronization to pulses from Master inverter. General description of Master - Slave synchronization of FR-A800 inverters with wiring diagrams and ...
PLC - GX Works 3 - Device Assignment Confirmation CC Link/CC Link IE TSN
This article describe Device Assignment Confirmation function in GX Works3 (GX Works2 works the same way), which helps to manage information about mapping of stations registers. Creating CC Link and CC Link IE TSN configuration, we the possibility to ...
MELSEC iQ-R Series Motion Module (RD78G) - Speed and torque control mode from the PLC side
MELSEC iQ-R Series Motion Module (RD78G) - Speed and torque control mode from the PLC side It is the article from the series Melsec iQ-R Series Motion Module (RD78G) Quick Start Guide. In this part you will learn how to: - controlling the speed of ...
INV - FR-E800 - Position control in Vector Mode
The article provides information on how to prepare the FR-E800 frequency converter and FR-A8AP -E-kit encoder card for positional vector operation. For details, refer to the manual: FR-E800 Instruction Manual (Function), Chapter 7 FR-A8AP E-kit card ...