Set the basic parameters that allow communication in the CC-Link IE Field Basic network. The basic parameters are listed in the table below.
| Parameter No. |
Parameter name |
Value |
| Pr. 79 |
Operation mode selection |
6 |
| Pr. 340 |
Communication startup mode selection |
10 |
| Pr. 544 |
CC-Link extended setting |
18 |
| Pr. 550 |
NET mode operation command source selection |
5 |
| Pr. 1427 |
Ethernet function selection 1 |
61450 |
You should also remember to set the IP address, as well as the subnet mask:
Also, specify the range of IP addresses that will be able to control the inverter:
The first step is to determine what communication parameters are selected in the master, i.e. in our case in the PLC. Depending on the driver, this is done in two different ways (GX Works2: FX3S, FX3G or GX Works3: FX5).
We open the project and in the Navigation tree select: Parameter-> PLC Parameter
In the newly opened window, go to the tab PLC System(2):
Here we have the parameters of our communication. We select the data we are interested in from it:
| Name |
Value from the screen |
Description |
| Communication speed |
38400 |
Speed of communication |
| Data Length |
8Bit |
Length of the data fram in one communication |
| Stop bit |
2Bit |
Number of stop bits |
| Parity |
Even |
Parity of data transmission |
| Protocol |
Non-protocol |
Means Mitsubishi Inverter Protocol |
2. Reading communication parameters in GX Works 3 (FX5_):
We open the project and in the Navigation tree we go to the field: Parameter -> FX5UCPU-> Module Parameter -> 485 Serial Port.
In the open tab, we will be able to read the data we are interested in:
| Name |
Description |
38400 |
| Data Length |
Length of data frame in one communication cycle |
| Stop bit |
1Bit |
| Parity |
Odd |
| Protocol |
MODBUS RTU |
Communication protocol |
3. Parameter setting in the inverter:
As an example, we will take the data read from the GX Works 3 program, that is:
| Name |
Description |
38400 |
| Data Length |
With the ModBus RTU protocol selected, this value is 8 bit |
| Stop bit |
1Bit |
| Parity |
Odd |
| Protocol |
MODBUS RTU |
Now set the inverter parameter values:
| Parameter |
Description |
Example value |
| 117 |
Station number ( individual for each inverter) Range 0-31 |
| 118 |
Communication Speed: Possibilities: 48 – 4800 96 – 9600 192 – 19200 384 – 38400 576 – 57600 768 – 76800 1152 – 115200 |
384 |
| 119 |
DataLength or stopbit: 0 – 8Bit/1StopBit 1 – 8Bit/2StopBit 10 – 7Bit/1StopBit 11 – 7Bit/2StopBit |
0 |
| 120 |
Parity 0 – None 1 – Odd 2 – Even |
1 |
| 121-123 |
TimeOut of communication, number of connection attempts,etc. |
9999 |
| 549 |
Communication protocol: 0 – Mitsubishi Inverter Protocol 1 – ModBus RTU |
1 |