PLC and PC communication via SLMP Protocol
Overview of document
Overview of PC and PLC communication via SLMP
The purpose of this document is to provide simple solution for PC and PLC communication via SLMP.
A the beginning, there will be presented how to set communication parameters in GX Works3 for SLMP protocol. Then it will be show how to read a registry value from PLC using Hercules SETUP utility program. In addition, presented document contains information how to create your own console application in C# language.
Example effects
SLMP communication using Hercules SETUP utility
SLMP communication via Console Application
Details of PC and PLC communication via SLMP
Parametrization in GX Works3
PC and PLC connection
To establish connection between PC and PLC:
Connect devices with Ethernet wire → Create new project for your PLC select → Select Online → Current Connection Destination…
For Direct Coupled Setting we need only to put IP Address of Adapter and confirm settings (if communication test was positive).
Otherwise select Other Connection Method (Open the specify Connection Destiny window) →  CPU Module Direct Couple Setting → select Ethernet → put IP Address → Yes
Remember to set IP Address of your PC in the same subnet as the PLC
Execute Communication Test  and confirm the settings.
Module Configuration
Double click on Module Configuration from the project tree → by drag and drop place hardware components that represent the actual state.
You can also select Online → Read Module Configuration from PLC.
Ethernet Port
To start using SLMP Protocol set parameters as follow:
Set External Device Configuration by double click on <Detailed Settings> next to this parameter.
Add SLMP Connection Module from Ethernet Devices by drag and drop it → set TCP protocol → set Port No. on 2000 → Close with Reflecting the Setting.
After this operations select Check and Apply.
Write to PLC...
To write your project to PLC  select Online →click Write to PLC... →  select  Parameter + Program(F) → Execute
Reset PLC and go to RUN mode.
Monitor D200 parameter
Add parameter D200 twice to the Watch window by clicking on the row and putting “D200”. For the first case choose Decimal display format, and Hexadecimal for second one. To monitor and change current value click on Start Monitoring.
Connection with PLC
Open Hercules SETUP utility application → select Test mode  → set Module IP: 192.168.3.250 (IP address of PLC set in GX Works3) → set Port: 2000 (as in Ethernet Configuration in GX Works3)
If you don’t have the application installed yet, here there is a link to the website with the software:
https://www.hw-group.com/software/hercules-setup-utility
Make sure that IP address and Port No. are the same as those set in GX Works3.
After this operation you should be able to start communication. To do this, press Connect.
Connection operation status will be displayed in Received data: Connected to 192.168.3.250 (PLC address).
Sending request to  PLC
Before you will send request to PLC, make sure the settings look like these:
Put the request into Send section:
“50 00 00 FF FF 03 00 0C 00 10 00 01 04 00 00 C8 00 00 A8 01 00”
Which is synonymous with:
Request
50
00
00
FF
FF
03
00
0C
00
Subheader
(without serial No.)
Request destination
network No.
Request destination station No.
Request destination module I/O No.
Request destination multidrop station No.
Request data length
Response
D0
00
00
FF
FF
03
00
04
00
10
00
01
04
00
00
C8
00
00
A8
01
00
Monitoring timer
Comand (0401:Read)
Subcommand
Head Device No.
 (0xC8 => 200DEC)
Device code (D register)
No. of device  points
00
00
BE
DC
Error code
Response data
Select Hex option and click Send.
In presented situation, sent command asks PLC about D200 register.
All sent commands are displayed in the Sent data section.
Data from the PLC are received and displayed in hexadecimal form in Received data section.
Observing  this register in Watch window in  GX Works3 you can confirm that data was sent properly.
C# Console Application
Run ready application
Write the IP address of PLC into byAdres[] as shown below → put ipAdress and 2000 (Port No. - value as in GX Works3 settings) as arguments of ConnectTCP function
using System;
using System.Net.Sockets;
using System.Net;
using System.Net.NetworkInformation;
namespace SLMP_SampleFrame
    class Program
        static TcpClient tcpC = new TcpClient(); // Global TcpClient object
        static void Main(string[] args)
            byte[] byAdres = new byte[4];
            // set IP address of PLC
            byAdres[0] = 192; byAdres[1] = 168; byAdres[2] = 3; byAdres[3] = 250;
            IPAddress ipAdress = new IPAddress(byAdres);
            ConnectTCP(ipAdress, 2000);//connection for set IP address and Port No.
            if(tcpC.Connected) //if TcpClient is connected perform next lines
                Read_D200(); // read D200 register
            Console.ReadKey();
Main program
In “Part of code for read D200 register” section, put the request into payload variable:
“0x50, 0x00, 0x00, 0xff, 0xff, 0x03, 0x00, 0x0C, 0x00, 0x10, 0x00, 0x01, 0x04, 0x00, 0x00, 0xC8, 0x00, 0x00, 0xA8, 0x01, 0x00”
Request
50
00
00
FF
FF
03
00
0C
00
Subheader
Request destination
network No.
Request data length
Response
D0
00
00
FF
FF
03
00
04
00
10
00
01
04
00
00
C8
00
00
A8
01
00
Monitoring timer
Comand (0401:Read)
Subcommand
Head Device No.
 (0xC8 => 200DEC)
00
00
BE
DC
Error code
Response data
Each byte in created table is hexadecimal and  separated by a comma.
#region Part of code for read D200 register
        static void Read_D200()
            //Request frame for read D200 register
            byte[] payload = new byte[] { 0x50, 0x00, 0x00, 0xff, 0xff, 0x03, 0x00, 0x0C, 0x00, 0x10, 0x00, 0x01, 0x04, 0x00, 0x00, 0xC8, 0x00, 0x00, 0xA8, 0x01, 0x00 };
            NetworkStream stream = tcpC.GetStream();
            stream.Write(payload, 0, payload.Length);
            byte[] data = new Byte[20];
            stream.ReadTimeout = 1000;
            try
                Int32 bytes = stream.Read(data, 0, data.Length);
                if (data[9] == 0 && data[10] == 0)
                    byte lowbyteResponse = data[11];
                    int hibyteResponse = data[12];
                    int afterConversion = (hibyteResponse << 8) + lowbyteResponse;
                    // Show information about D200 register and operation status
                    Console.WriteLine("Read D200 finished correct!");
                    Console.WriteLine("Readed value D200 (HEX): Hi byte[" + hibyteResponse.ToString("X") + "], Low byte [" + lowbyteResponse.ToString("X") + "]");
                    Console.WriteLine("Readed value D200 (DEC + Converted): " + afterConversion.ToString());
                else
                    Console.WriteLine("Error in Answere");
            catch
                Console.WriteLine("Error in interpreter");
        #endregion
Launch your application.
Data from the PLC are received and displayed in console. Firstly in hexadecimal form, detail Low and High byte. Secondly this bytes are converted and displayed in decimal form.
Before displaying register value, information about operation status is shown.
Caution!
Presented code is only a sample program, so it should not be run directly on a real object! Customize the created application to your needs.
The number of sent and receive data can vary. In presented example, the number of frame elements is static.
Modifications
MakePingTest
Adding this function will make establishing a connection easier. User gets information whether the device responds.
#region Function for perform Ping test with real PLC
        static bool MakePingTest(IPAddress IPAddressForTest)
            bool pingAns = false;
            Ping pingSender = new Ping();
            PingReply reply = pingSender.Send(IPAddressForTest);
            if (reply.Status == IPStatus.Success)
                pingAns = true;
            return pingAns;
        #endregion
SelfTest
You can also add function that will check the correctness of the sent data frame. This function compares sent and received data (in this case the test is performed on a 5-element set). If data match, then data can be exchanged between devices and communication starts
       #region Part of code used to verify whether the communication function operates normally or not
        static bool SelfTest()
            bool loopTestAns = false;
            byte[] loopMessage = new byte[5] {0x41, 0x42, 0x43,0x44, 0x45}; // 5 elements for test - "ABCDE"
            //Request data length
            int needByteMessage = 2 + 4 + 2 + loopMessage.Length;
            byte lowByte = (byte)(needByteMessage & 0xff);
            byte highByte = (byte)(needByteMessage >> 8 & 0xff);
            byte[] payload = new byte[] { 0x50, 0x00, 0x00, 0xff, 0xff, 0x03, 0x00, lowByte, highByte, 0x10, 0x00, 0x19, 0x06,0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00 };
            //number of loopack data
            lowByte = (byte)(loopMessage.Length & 0xff);
            highByte = (byte)(loopMessage.Length >> 8 & 0xff);
            payload[15] = lowByte; payload[16] = highByte;
            // loopack data
            for (int i = 0; i < loopMessage.Length; i++)
                payload[17 + i] = loopMessage[i];
            try
                if (data[9] == 0 && data[10] == 0 && data[11] == lowByte && data[12] == highByte)
                    loopTestAns = true;
                        if (loopMessage[i] != data[13 + i])
            catch
            return loopTestAns;
        #endregion
Function for check the correctness of the sent data frame
Simple library
It is possible to use simple library. All data you can find in attached file: „Simple Library for SLMP communication.zip”. Inside you can find necessary DLL file to import your project and sample program where this library was used.