GOC43 Communication - CCLIEFB setup
This article will guide you how to setup GOC43CCLIEFB communication with FR-E800E step by step.
Copyright © Mitsubishi Electric Europe B.V.
These Function Blocks / programs are demo versions that are only  intended to demonstrate program functions and provide general orientation for  your software choices. They are not suitable for use in real applications! "
1. GOC 43 CCLIEFB Master
    1.1  Create a new project
      Select Device and programming language
      1.2 Add Library to the project
      After project created, please add GOC43_CCB library tot he project
      1.3 Add FB to the POU
      Open Ladder program and drag & drop Box element to he first ladder network
      Search for CCLIEFB_master_config FB
      After add one instance into the variable table of that FB
      Copy these variables to the VAR section:
      (For testing purpose Stn No.:= 5 we will use FR-E800E inverter, which is occupied 1 station)
            bEnable : BOOL;
            (* CCB *)
            CCLIEFBasic_Master_Config_0: CCLIEFBasic_Master_Config;
            (*FB input*)
            NumOfStation : BYTE := 1 ;        (* Define number of stations connected *)
            CCBStationList: ARRAY [0..3] OF CCLIEFBasicStation := [(Stn_No := 5, Occupied_Stn := 1),(Stn_No := 2, Occupied_Stn := 1),(Stn_No := 3, Occupied_Stn := 1),(Stn_No := 4, Occupied_Stn := 1)];
            TimeoutPeriod: WORD := 1500 ;                                             (* Define communication timeout period*)
            NoOfRetries: Count := 0;                                                             (* Define number of retried Count_0 =3 retries,Count_1=5 retries, Count_2=10 retries *)
            ResetMasterDiag: BYTE;        (* Reset master diagnostics as 0: No reset action, 1 : Reset max, min Link scan time, 2: Clear latest error code, 3: 1+2 *)
            CCB_SlaveInfo: ARRAY [0..3] OF CCLIEFBasic_DiagInfo; (* Monitor CC-Link IEF Basic diagnostics of individual slave station *)
            (*FB output*)
            MasterConfigDn: BOOL;                                                              (* TRUE : Master config dn successful, FALSE : Master config. unsuccessful*)
            Error_MasterConfig: BYTE;                                 (* Monitor cause of error in configuration *)
            Error_Com: BYTE;        (* Monitor cause of error in communication *)
            MaxLinkScanTime: WORD;                                                        (* Monitor maximum Link scan time*)
            MinLinkScanTime: WORD;                                                         (* Monitor minimum Link scan time*)
            CurLinkScanTime: WORD;                                                         (* Monitor current Link scan time*)
            RXArray AT %MW3000: ARRAY [0..3] OF WORD;                                 (*RX data*)
            RYArray AT %MW4000: ARRAY [0..3] OF WORD;                                 (*RY data*)
            RWrArray AT %MW5000: ARRAY [0..31] OF WORD;                           (*RWr data*)
            RWwArray AT %MW6000: ARRAY [0..31] OF WORD;                         (*RWw data*)
      Setup the FB input and output with variables, as the below picture
      1.4 Compile the project and download
      Download project to GOC43
      First establish connection with your plc
      PLC settings
      Then login, and download your project
      Start PLC
      During download and stop mode GOC43 will show the system info
2. Setup FR-E800-E CCLIEFB Slave station
      2.1 Create a new project and connect to the inverter
      Connect mini usb cable to the inverter
      2.2 Read out parameters
       Open parameters, then go Online. After that read batch parameters
      2.3 Setup and write parameters t the inverter
      Setup the following parameters from the default
            Pr.544 = 18        (ver 2)
            Pr.1429 = 61450             (CCLIEFB)
           IP of the inverter
                  Pr.1436 = 3        (3rd octet of IP)
                  Pr.1437 = 5        (4th octet of IP)
            IP of the controlling devices
                  Pr.1449 = 192
                  Pr.1450 = 168
                  Pr.1451 = 3
                  Pr.1452 = 1
                  Pr.1453 = 3
                  Pr.1454 = 254
            Change operation mode to PU before start batch write
      After writing of the parameters finished change back the operation mode to NET
      Disconnect USB cable, and if inverter has error, please press stop/reset button (red).
3. Test
      Test communication with running of the inverter. So we will enable first communiction then turn on forward bit
      3.1 Tur on com. enable bit
      If we did everything fine, and inverter is not in error (for example E.EHR), we need to see the following status of the FB. Fb output done means communication established and linkScantime show some values
      If we have some errors error config output will have a value. Every value has it’s own meaning. If you keep mouse on the output description will be shown.
      3.2 Let's start our motor/inverter (FWD) command
            Manual contains the necessary bit for this test, here you can see the control and status bits of the inverter via CCLIEFB
            Word registers for controlling and monitoring
              So turn on first bit of the control word and we will see the inverter start operating the motor, in the example the set freuqency was 23.00Hz
      Ready Program and inverter parameters attached.